I would suggest you read the actual rule in the NEC code book for completeness.
Buy NFPA 70, National Electrical Code (NEC) Handbook
Order the NFPA 70, National Electrical Code Handbook. The Handbook explains the NEC fully and is available in various print and digital formats.catalog.nfpa.org
I found this: Sizing a Circuit Breaker
"NEC sizing rules. Secs. 210-22(c), 220-3(a), 220-10(b), and 384-16(c) all relate to the sizing rules for overcurrent protective devices (OCPDs). The first three all specify the same requirement:
Sec. 384-16(c) has the same requirement, except that it's stated in terms of the loading of the OCPD. This rule states that an OCPD can be loaded to only 80% of its rating for continuous loads. Remember that 80% is the inverse of 125% (0.80 = 1 ÷ 1.25) and, as such, the rules are indeed identical in their end requirement.OCPD size = 100% of noncontinuous load + 125% of continuous load.
Read the rule closely; the 125% sizing of the OCPD (or 80% loading) is only applicable when continuous loads are involved. CBs and other OCPDs can be sized at 100% of their rating for noncontinuous load applications."
So you are generally correct, but that does not take the power factor into account (which Gene claimed to be 0.75 for a typical AVR). Try this calculator with sample 1,000 W loads of various non-continuous types, and a 120 V circuit single-phase AC, and see how that affects CB size. With the PF=0.75, the CB is 1.33x that with PF=1, all other things being equal. What do you think the safety factor (SF) should be for AVRs? Higher than the 75% for AC or even 100% for a welders (an even more non-continuous load)?