Or watch the video of the owner of Zero Surge above in post #35. The tech in all the others is directly from Zero Surge.Suggest reviewing the papers on the Series mode designs deployed by BrickWall, ZeroSurge and SurgeX.
Or watch the video of the owner of Zero Surge above in post #35. The tech in all the others is directly from Zero Surge.Suggest reviewing the papers on the Series mode designs deployed by BrickWall, ZeroSurge and SurgeX.
Suggest reviewing the papers on the Series mode designs deployed by BrickWall, ZeroSurge and SurgeX.
For brief drops and gen kick-in time, you need a good sine-wave UPS to step in as the failure is detected and when a generator can crank and pick up the load. This is pretty much standard operating designs we've used in datacenters for decades. On the UPS, be prepared to replace the batteries every 3-4 years depending on many factors like storage, operating temps etc.. I've found that my smaller 1200VA Sine-wave UPSes at home go thru batts about every 36 months.
I think a UPS is more like the solution I am looking for. Something that will protect against mild fluctuations and, in the event of a quick off/on cycle, allow me to power everything down correctly.
When you say sine-wave UPS are you referring to on-line UPS' that are always running?
In addition to the zerosurge and furman that the equip is plugged into, I mounted one of these in the breaker box....
CHSPT2ULTRA
Eaton SPD Type 2 CHSP Service Entrance Surge Protection, 120/240V line, 150V L-N, 300V L-L MCOV, 600V L-N, 1000V L-L, 800V N-G, 600V L-G VPR, 22 kA SCCR, NEMA 4, Single-phase, 60 Hz, 20 kA nominal current discharge, 108 kA surge current
![]()
I've got a couple of these cheap APC UPS I've had the odd brown out where its flipped over to battery which seems like a good thing, and its ground fault check works, let me know my upstairs sockets weren't grounded (yes a $5 checker can also do that). So its already doing some good. I like to think it will handle a little surge as well (now that I fixed the ground wiring)
Does a surge protector require a three-prong grounded outlet, and/or are there any designs that work in non grounded, two prong situations?
Thanks for the response. Is it possible to have no ground though? I haven’t seen any outlet that has a third wire going to it. So where would the ground likely be?A grounded outlet is not required. If your outlet is not grounded you can only protect the line-neutral connection which is often enough indoors as neutral and ground in the house are bonded.
Thanks for the response. Is it possible to have no ground though? I haven’t seen any outlet that has a third wire going to it. So where would the ground likely be?
I am looking at the outlets here in Central America where brown-outs are quite frequent. No third wire going to any of them.Huh? All outlets have 3rd wires going to them in anything constructed in the last 50+ years. Some products don't use a 3rd prong because they typically have plastic cases and everything is double insulated.
I am looking at the outlets here in Central America where brown-outs are quite frequent. No third wire going to any of them.
For example...Unfortunately you are at a state where we were about 50+ years ago, maybe 60+. I know being in a few countries in Central America, AC wiring is pretty dicey.
Series protector similar to surgeX products. No failure prone MOV's. I would consider whole house protection at the power panel.Another vote for zero surge.