• WANTED: Happy members who like to discuss audio and other topics related to our interest. Desire to learn and share knowledge of science required. There are many reviews of audio hardware and expert members to help answer your questions. Click here to have your audio equipment measured for free!

Circuit breaker - which to choose

OP
R

roxor

Member
Joined
May 21, 2023
Messages
66
Likes
1
The pros and cons and safety of using a high-amp electric device that was designed for a safety ground and is using neutral is beyond what I would want to comment on. I know there are ppl on the forum who work with that stuff and know it.
so you are suggesting that i should immediately use floating earth ie separate line for ground?
ah okay, in that case i will have to make rewire everything.
 

radix

Major Contributor
Joined
Aug 1, 2021
Messages
1,409
Likes
1,349
so you are suggesting that i should immediately use floating earth ie separate line for ground?
ah okay, in that case i will have to make rewire everything.
No, I'm not saying to float the earth. That has all sorts of other problems, as you can build up a charge on the case from the magnetic field.

The best thing would be to get a proper 3-conductor outlet. But I'd defer to someone who really knows consumer electronics safety about using it with a N+E bridge.

In regards the to link, it's probably home depot trying to do location-dependent service. Just google "gfci without ground."
 
OP
R

roxor

Member
Joined
May 21, 2023
Messages
66
Likes
1
@radix maybe i dont know whats floating ... to float the earth mean?

what is a proper 3-conductor outlet?
 
OP
R

roxor

Member
Joined
May 21, 2023
Messages
66
Likes
1
Try this one.
insane even i google it .. it shows the link / partially content but i cant open it ;/
 

NTK

Major Contributor
Forum Donor
Joined
Aug 11, 2019
Messages
2,719
Likes
6,013
Location
US East
insane even i google it .. it shows the link / partially content but i cant open it ;/
I am copying the section on GFCI working without ground here:
Will a GFCI Work Without a Ground?​
A ground is not required for a GFCI to function. GFCI devices work by detecting the current flowing from the hot to the neutral wires. Any imbalance trips the device, so a ground is not required. Older homes and buildings not designed to current electrical codes can still have GFCI protection.​
GFCI outlets installed without a ground may not trip when inspected with a voltage tester, which do require grounds to work. The device can be tested with the test button integrated in the outlet.​
To fully comply with NEC regulations, GFCI devices installed without grounds must be marked “GFCI Protected” and “No Equipment Ground” on the plate.​
 

audio_tony

Addicted to Fun and Learning
Joined
Feb 24, 2019
Messages
576
Likes
697
Location
Leeds, UK
argh,.. Its connected to the neutral.
In the UK most installations use the TN-C-S grounding system (earth to neutral).

Which country are you in, as the regulations for your country will state how your home should be grounded.

Please be careful about taking advice about grounding schemes and earth leakage detection using an earth leakage circuit breaker, as standards may vary from country to country.

An earth leakage breaker in the UK is rated to trip at 30mA (that means that if it detects 30mA of current flow to ground it will trip).

1710195345549.png
 
Last edited:

JustJones

Major Contributor
Forum Donor
Joined
Mar 31, 2020
Messages
1,746
Likes
2,468
@voodooless

My wall 230V sockets contains 2 cables, ie L and one more cable which is used to bridge N+E,
as per my understanding i wont be able to use CB with GFCI,
in case i want to use the one with GFCI then i need to rewire flat, and each 230V wall socket has to be connected to 3 separate lines ie L, N, E.


appreciate
View attachment 355713

This looks like North American type breaker and receptacle. I thought you are in EU ?

Contact a reputable local electrician and explain what's going on. I would hope they would know the appropriate breaker you need.
 
OP
R

roxor

Member
Joined
May 21, 2023
Messages
66
Likes
1
In the UK most installations use the TN-C-S grounding system (earth to neutral).

Which country are you in, as the regulations for your country will state how your home should be grounded.

Please be careful about taking advice about grounding schemes and earth leakage detection using an earth leakage circuit breaker, as standards may vary from country to country.

An earth leakage breaker in the UK is rated to trip at 30mA (that means that if it detects 30mA of current flow to ground it will trip).

View attachment 355765
at the moment Czechia.
 
OP
R

roxor

Member
Joined
May 21, 2023
Messages
66
Likes
1
This looks like North American type breaker and receptacle. I thought you are in EU ?

Contact a reputable local electrician and explain what's going on. I would hope they would know the appropriate breaker you need.
currently EU - Czechia.
ah u guys dont know what kind of ppl/ experts and technicians live here :)
 
Last edited:

Blumlein 88

Grand Contributor
Forum Donor
Joined
Feb 23, 2016
Messages
20,784
Likes
37,678
There are such devices, but none AFAIK are consumer addons. They are rather inexpensive circuit elements, so I don't know why MF would not have used them. -- maybe they did and your's is bad?


AFAIK, we only have one photo of inside the PSU, but there are other things in there besides the transformers. Without a service manual or detailed photos, I don't think one can say much about what might or might not be causing the problem.
They used choke style power supply.
 

radix

Major Contributor
Joined
Aug 1, 2021
Messages
1,409
Likes
1,349
@radix maybe i dont know whats floating ... to float the earth mean?

what is a proper 3-conductor outlet?

I'm going to speak about the USA, which is what I know.

Here, we get L1, L2, and N from the utility. It's 110-120V per L1 and L2, or 220-240V for a 4-wire system like a dryer or induction cooktop.

At the entry to the home, there is an earth ground, G, (a long copper rod in the ground). N is tied to G at that one place, the main service panel at the entry of the house. Every outlet gets L (either L1 or L2), N, and G. Sub-panels also keep N and G separate. In this setup, all current flows via L1/L2 and N.

In the old days, it was only 2-wire (L + N) per outlet. Or sometimes G would be tied to different ground rods under the house.

Under normal conditions, G carries no current to/from an outlet. If there is an electrical fault, current will be shunted to G. This causes GFCI breakers or outlets to trip. If there is not a G (you only have L and N), then the fault is usually via a poor person who touched something bad, or for example, if there is a short to the metal case and a person touches the metal case.

If you only have 2 conductors to an outlet in your building, that means they either floated G or tied G to N at the outlet. By floating G, I mean not connecting it to anything.

If a product is designed to have an earth ground, then floating G is likely dangerous. If it is a 2-wire consumer product designed for use without a G, then they have hopefully taken proper precautions to protect the consumer from a fault, like using a plastic or non-conductive case and controls.

There's a fair bit of engineering that goes into electrical safety of consumer products that I'm not very familiar with, so please don't take anything I say as a recommendation to do something.

If G is tied to N at the outlet, and you draw 100A inrush, that will create a voltage difference over your wire in the wall. If that 100A is on the ground terminal, then the metal case of your system will see that voltage. Let's say you have 0.5 ohms of wire in the wall. V=IR => V = 50V. It's super brief, but not safe, in my opinion. If G is floating, you might still induce a voltage in the metal case from the transformers.

So, if you are sure that your outlet only has 2 wires, not hot + neutral + ground, then you might want to ask an electrician in your area about getting a proper ground run. That will put the metal case at near 0V even when you have 100A running between hot + neutral.
 

audio_tony

Addicted to Fun and Learning
Joined
Feb 24, 2019
Messages
576
Likes
697
Location
Leeds, UK
at the moment Czechia.
I searched for electrical regulations in Czechia and the closest I could find was this forum post from 2011

It looks as though whatever earthing system you have will be defined by the age of the building you live in.

 
OP
R

roxor

Member
Joined
May 21, 2023
Messages
66
Likes
1
hi,
i found some more detail in the revision report from the whole building and there is stated:
1710319736590.png
 

radix

Major Contributor
Joined
Aug 1, 2021
Messages
1,409
Likes
1,349
hi,
i found some more detail in the revision report from the whole building and there is stated:
View attachment 356075

See https://www.asutpp.com/pen-conductor.html

You need an electrician to look at how your specific outlets and panels are wired.

The TNC/TNCS and PEN/PE+N generally describe how the utility delivers power to the building. You can split a PEN to a PE+N at the main distribution panel. All you really care about is if a particular outlet has a current-carrying protective ground or a split non-current carrying protective ground.

You can have a PEN (where the N and PE and bridged) or a PE+N (where the PE and N are separate) depending on how it was wired. If you have a 2-conductor outlet, then its bridged. If you have a 2-conductor with exposed ground, then you have a separate PE return.

There's many ways buildings are wired and it changes over time. I would never trust a label on something much less an as-built plan. You need someone to look.
 
OP
R

roxor

Member
Joined
May 21, 2023
Messages
66
Likes
1
@radix thanks
i will have electrician visit, is it possible formulate
what exactly do i have to require ie what Ground setup would be best so i can task that to him?

just to articulate requirements to him ... and also i believe there is 3phase option.



Thanks
 

radix

Major Contributor
Joined
Aug 1, 2021
Messages
1,409
Likes
1,349
@radix thanks
i will have electrician visit, is it possible formulate
what exactly do i have to require ie what Ground setup would be best so i can task that to him?

just to articulate requirements to him ... and also i believe there is 3phase option.



Thanks

If you have a large inrush current, then IMO a current carrying protective earth ground for a metal chassis is not ideal. It will build up a voltage during that period. Let's say you have 2mm (12 AWG) copper wire and the distance is 10m to the protective ground (just to make the math easier). 12 AWG wire will be about 5 ohms / 1000m, so you have 0.05 ohms in the wire. If the inrush current is 100A, then you have V=IR = 5V. In the previous example I gave, I had a much higher resistance. Maybe 5V is OK, maybe you'll fell it if you touch the case. Again, all those numbers are just an example. I do not know the wiring codes where you are, so it may not even be an option to switch your grounding. Or it may be you have to run all the way to the distribution panel and it is not economically practical.

3-phase is a totally different beast. Only specialized equipment uses 3-phase. You may very well have 3-phase coming in to the building that is then converted for used by individual branches. That's 220V per phase, or 400V between phases, so you could get massive power out of it. I believe in the EU, each single phase is simply one of the 3-phase loads (i.e. L1+N, L2+N, L3+N is 3 single phase loads). In the US, 3-phase to 1-phase requires a transformer if it's 480Y/277V not 208Y/120V. And it also depends on if it's 3-wire (delta) or 4-wire (wye) service. It gets complicated and is very dangerous.

As I've mentioned, I'm not an electrician so nothing I say should be considered advice (apart from where I say talk to an electrician!).

I would explain the situation to him: I have an amplifier with large toroidal transformers that seems to have a large inrush current, as it sometimes trips the breaker. Do I have a non-current carrying protective earth? if not, should I get one and how much $? Should I switch to a slower circuit breaker?

He should be able to inspect your panel and your outlet and let you know what can be done.

Have you inspected the fuses in the PSU, and are they the correct ones?
 
OP
R

roxor

Member
Joined
May 21, 2023
Messages
66
Likes
1
See https://www.asutpp.com/pen-conductor.html

You need an electrician to look at how your specific outlets and panels are wired.

The TNC/TNCS and PEN/PE+N generally describe how the utility delivers power to the building. You can split a PEN to a PE+N at the main distribution panel. All you really care about is if a particular outlet has a current-carrying protective ground or a split non-current carrying protective ground.

You can have a PEN (where the N and PE and bridged) or a PE+N (where the PE and N are separate) depending on how it was wired. If you have a 2-conductor outlet, then its bridged. If you have a 2-conductor with exposed ground, then you have a separate PE return.

There's many ways buildings are wired and it changes over time. I would never trust a label on something much less an as-built plan. You need someone to look.
the guy was here ...
he said i have 2x25A or 1x25A option

He mentioned that main connect is TN-C and then he mentioned that ground will be as PEN where P/ E/ N each will be separate to the wall sockets..
is that okay?
thanks
 
Top Bottom