Need Exhaust Fan That Has Soundproof Properties

Long story short, I need an intake fan to bring in fresh air(oxygen) inside my apartment in which the carbon monoxide increases once there is more than one person inside. I know, why don't I open windows but the air quality is horrendous in my country during winter so I am looking at an exhaust fan that has a HEPA filter so filtered air is brought inside. I know basic forms of this exist however I need something that has soundproof properties through the length of the fan tubing.

Now the problem is that I will put this fan in my corridor which has open windows however I do not want general noise from the corridor to leak into the apartment from that opening. T

The wall is about 60cm thick so the fan will need to be approximately that in length, is there such a thing available in the market that will draw air inside fromoutside through a HEPA filter but also has some soundproofing qualities through the tube?

I do have other options I have 3 exhaust ventilation, kitchen, bathroom and a spare outlet for gas which I am not allowed to touch. With this option air can be sucked in through these points air from the roof so no sound however I can't see how these can be used. Don't want to be pulling in air from the kitchen ventilation as I will pull in all the oil and grease that is being pulled out. For now, I am exploring this option. Any ideas on a product like this?

I know exhaust fans such as this exist just not sure if they have soundproof properties.
If you want to keep it energy-efficient, look for a system with a heat exchanger (it uses waste heat from a furnace or water heater to heat the incoming air from outside). Otherwise, just sucking in cold air from outside could be expected to raise your heating bill significantly.
 
I'm not an expert on this, but for noise reduction you probably need a baffled duct, similar to a car muffler. I'm not sure if this will fit inside a 60cm wall, but without that you probably will hear noise through the duct.

I have air quality monitors in my house. I also notice the CO2 going up fast when there is more than one person in a room. What I do is open the window and turn on the kitchen and bathroom vent fans to clear the air fast. Then I close the window again. I have a few HEPA air purifiers in the house to deal with any PM2.5 that comes in. The air in my area is generally not TOO bad so it's not a big deal to have some outdoor air to come in. But if you get a few good stand alone HEPA filters in your house, you can deal with PM2.5 in an hour or two.
 
If you want to keep it energy-efficient, look for a system with a heat exchanger (it uses waste heat from a furnace or water heater to heat the incoming air from outside). Otherwise, just sucking in cold air from outside could be expected to raise your heating bill significantly.
Can you provide me a link so I can check out what your describing?
 
I'm not an expert on this, but for noise reduction you probably need a baffled duct, similar to a car muffler. I'm not sure if this will fit inside a 60cm wall, but without that you probably will hear noise through the duct.
I am worried about noise entering through the duct.
I have air quality monitors in my house. I also notice the CO2 going up fast when there is more than one person in a room. What I do is open the window and turn on the kitchen and bathroom vent fans to clear the air fast. Then I close the window again. I have a few HEPA air purifiers in the house to deal with any PM2.5 that comes in. The air in my area is generally not TOO bad so it's not a big deal to have some outdoor air to come in. But if you get a few good stand alone HEPA filters in your house, you can deal with PM2.5 in an hour or two.
I manage to bring down PM2.5 down within 30 min with 2 large filters and a small one and I also fly screens that apparently block out to about PM2(but also reduce air flow and makes it harder to get air back in to make up for C02) and funnily enough they do work up until the neighbors start heating/using wood fire the smoke just comes straight in. Technically I do what your saying but need to manage it outside the hours my neighbors are using wood fire and it works not a bad way to go about it.
 
Remember, the fan can be anywhere. One end of a tube, the other end, in the middle. A different location can make a big difference in noise that affects others.


You do NOT need a lot of flow, just a steady flow. A steady flow will keep things from building up. To clear a lot of volume quickly takes a lot more. So aim to keep things from building up.

First thing I would check would be to see if the kitchen fan and/or the bathroom fan will create enough flow from the building to outside. Given the type of building, I am going to guess you get flow into your place from the hallway via the door. If you are OK with the inside air, no need to filter.

Then you can see about making those fans less noisy. Or one of them.
Instead of pulling air from outside have you considered pulling air or circulating from the inside common area of your building. As an experiment what happens if you turn on an existing exhaust fan while the hallway door is cracked?
I think these posts are not receiving enough attention. How the heck is the apartment vented right now? If there are exhaust fans in kitchen and bathroom, is there a vent to the corridor when air is being drawn in? Or a gap under the door?

Use the fans you already have to move the air when you are concerned about an air quality issue. Unless the corridor is actually exterior to the envelope you should be drawing in air that has already been conditioned for the corridor space. If the air supply is through an exterior wall, there is like a filter already, although it may or may not get replaced or cleaned on a regular basis.

Try to use what you should already have. If the noise from the kitchen or bathroom fans is an issue, that may not be easy to address, though. Well, the way to address it is with a fan installed on the exterior (a 'remote fan') instead of in the ceiling of your apartment. But the landlord may not allow that -- the main issue is power would need to be run to it. But dang, remote fans are quiet as heck within the interior space.

[EDIT -- if the issue is the current interior fans suck in smoke, etc. through whatever the current intake is located, that needs to be dealt with (likely with filters). Not simple if the air is drawn in under the exterior door, but hopefully that 100% is not the case as that is not how fresh air should be provided.
 
I once lived in an apartment next to a train line and busy highway in Sydney. The main bathroom fan went 24x7. That was enough to get a permanent layer of soot on the carpet next to the front door as it tried to draw air in from underneath it.
 
I once lived in an apartment with no ventilation to the exterior at all unless you opened the windows. And the hallway had a strong odor of cigarettes, dead mice, and glade plugins. Definitely more than the sum of its parts. I put weather stripping on my hall door to block it. Didn't stay there long.
 
I think these posts are not receiving enough attention. How the heck is the apartment vented right now? If there are exhaust fans in kitchen and bathroom, is there a vent to the corridor when air is being drawn in? Or a gap under the door?
Firstly the corridor is technically outside so that idea is not possible. Secondly, the vents of both the bathroom and kitchen lead to the roof which is the 5th floor. When you say vented do you mean general fresh air or just genral getitng air out? If you mean getting air out then there is an exhaust fan in the kitchen and bathroom and a third which is for a case leak that doesn't have a fan connected its just an outlet. But these vents are 50 years old don't have proper piping and not really sure how there built but they work.
Use the fans you already have to move the air when you are concerned about an air quality issue. Unless the corridor is actually exterior to the envelope you should be drawing in air that has already been conditioned for the corridor space. If the air supply is through an exterior wall, there is like a filter already, although it may or may not get replaced or cleaned on a regular basis.

Try to use what you should already have. If the noise from the kitchen or bathroom fans is an issue, that may not be easy to address, though. Well, the way to address it is with a fan installed on the exterior (a 'remote fan') instead of in the ceiling of your apartment. But the landlord may not allow that -- the main issue is power would need to be run to it. But dang, remote fans are quiet as heck within the interior space.
It seems that my soundproof muffled vent idea is just too difficult as someone mentioned a 60cm wall needs drilling and the cost of those muffled silencers seem expensive. However, I can have a filtered fan on the back side which is fairly quiet, this was not my preferred option as it is in the kids room and the wall is near the entrance of the building so people can talk and noise will get through but it is a much simpler option of putting something like the heat recovery ventilation with a HEPA filter that someone linked. If I get noise from that gap then it is what it is.
[EDIT -- if the issue is the current interior fans suck in smoke, etc. through whatever the current intake is located, that needs to be dealt with (likely with filters). Not simple if the air is drawn in under the exterior door, but hopefully that 100% is not the case as that is not how fresh air should be provided.
Fresh air is generally provided by opening the windows but its just a hassle to turn my air purifiers on for 45 min to bring the bad air quality down. And then the carbon dioxide increases back up to 1000 in 30 min, kind of like slamming my head against a brick wall. So I really need filtered air coming in and it looks like I will put it in the back where the sound issue of cars etc is not that bad.
 
It seems most of the options only have an F7 filter, I used chat gpt and it seems that with around 150 PM 2.5 levels outside it might not be effective enough? But then again, better than nothing the air purifiers can do the rest of the job.
 
Firstly the corridor is technically outside so that idea is not possible. Secondly, the vents of both the bathroom and kitchen lead to the roof which is the 5th floor. When you say vented do you mean general fresh air or just genral getitng air out? If you mean getting air out then there is an exhaust fan in the kitchen and bathroom and a third which is for a case leak that doesn't have a fan connected its just an outlet. But these vents are 50 years old don't have proper piping and not really sure how there built but they work.
The bathroom and kitchen fans exhaust air out of the apartment. That reduces the air pressure inside the apartment, so air will get pulled in to equalize the pressure. If there isn't an intake vent, then it is infiltrating in through door and window openings, poorly-sealed exterior walls, etc.

If there is currently no real intake vent, and you increase the exhaust, more unfiltered/ untreated air will be drawn inside. That may or may not be an issue depending on the climate, outside air quality, etc. Houses here in the US typically do not have air intakes, but apartments usually do unless they were built before the 1950s. Some have vents opening into common interior areas (corridors, etc.) or central shafts, and others draw through the exterior walls directly into wall-mounted radiator enclosures. Please note I am not a mechanical engineer, but I see a lot of the systems when we are troubleshooting exterior walls.
 
Houses here in the US typically do not have air intakes, but apartments usually do unless they were built before the 1950s.
Seems to be different over here then. My apartment block with bathroom exhaust fans (because windowless) was built in 1992, and AFAICT there were no special provisions made for these. I generally tilt the closest window while I'm in the bath. When the windows were replaced during major renovations last year, they cut out part of the window gaskets on one window per room to allow for forced ventilation. It's not the most ideal solution since it compromises sound isolation (and needlessly so in the living room which has a pretty much airtight door) and isn't likely to improve the thermal side either, but I guess this is the best they could do under the circumstances. Having your windows replaced while you're living in there was quite the hassle as-is, I don't think any major construction work beyond that would have been very warmly received.
 
Appreciate everyone's reply and I have come to the conclusion that the product (Vakio Window Smart) that sells in my country is actually not a bad option at all. It has the fan outside the wall which will help with the fan sound and it also has damping material which could help with outside sound as it has to travel thorough the outside box and the inside box with a filter. I only saw this in you tube reviews, funnily enough there is no mention of it on their website, you would think it would be a selling point however it was in Russian so maybe google translate missed something. The fan has various options between consistent forced air supply to a rotating one(drawn in then out with 40sec intervals) and the air is heated in the rotating option. Should do the job, plus I can put in on the back wall which already has little noise and if the damping provides around 20db reduction(no spec unfortunately) well that's not much different than the windows. Furthermore the wall thickness isn't as thick as the side wall where I originally wanted it, so less drilling.

The only problem is that the fresh air might not fully make it to the main room, its a small apartment 40m2 and the room which it will be in is 10m2 with a large door opening of 2 meters in length to the main room which is only about 20m2. So its possible, plus if there is positive pressure it might find its way to the main room as the front door(front of the apartment) has air gaps however there is also two vents in the kitchen on the way to the front door so it could also possibly vent out through those rather than the air making its way to the front door.

 