Earth, grounding and dedicated AC mains

babysnake

Member
Joined
Oct 30, 2018
Messages
40
Likes
14
Can I ask the EEs and other technically informed forum members some questions about mains, earth and grounding of which there seems to be huge amounts of dis/misinformation and confusion on the 'Net, even by the standards of our hobby?

1
If one has the opportunity (which I luckily may well do) to have a dedicated mains for audio (by which I mean one that can be physically and electrically separate from the rest of the house mains) what should I be asking my electrician to do?

2
In the context of 1) above, should I be looking at a dedicated earthing rod in the garden (assuming that doesn't contravene building regs here in the UK)?

3
Much is written about, and a number of products both active (Telos) and passive (Entreq, CAD) exist, which claim to improve SQ (that old chestnut ;)) by providing a separate 'signal ground'. In essence they claim to work by attaching a device (PC, DAC or whatever) to what is allegedly a 'clean' 0v ground (achieved with clever electronics or mysterious minerals) via a dedicated cable (RCA, XLR, USB etc) to a spare device input. The apparent science here is that as all the signals in the attached box are referenced to signal ground, a 'clean' ground is advantageous as the internal electronics now have constant reference point (what did they use before, I wonder?). All sounds, on the face of it, pretty plausible, especially to someone like me with just enough science background to understand the logic, but crucially not enough to critically evaluate the claims !!! What do members think?

4 (Finally)
Notwithstanding the answers to the above, what methods/techniques can be scientifically applied to provide delicate electronic devices with clean, noise free earth/ground and mains? AC regenerators seem the obvious way to go, but reports are very mixed although it does seem fairly well accepted that these are worthwhile goals

If any of the above seems laughably confused, I apologise, but I would nonetheless be very interested in the views/opinions of those more technically proficient than I

Many thanks
 

RayDunzl

Grand Contributor
Central Scrutinizer
Joined
Mar 9, 2016
Messages
13,250
Likes
17,186
Location
Riverview FL
1. Ask to install a dedicated outlet - a new breaker and an unbroken three wire cable of maximum allowable gauge from the big box in the garage (whereever) to a new outlet at your gear.

2. No

3. Probably no, haven't seen much in the way of objective measures. There might be a couple here at ASR.

Ah, here's one - https://www.audiosciencereview.com/...ignal-grounding-preliminary-measurements.476/

4. Regenerators can provide a nice clean (even adjustable) source. Powerful regens aren't cheap,


Opinion:
First, determine you have a problem correctable by non-infected AC, only then should you investigate solutions.

In my case, I like the idea of an isolation transformer, one that floats/re-references the AC power to the gear above/around the Earth at that point.


*disclaimer - I have an Equitech balanced power isolation transformer in the rack, just because. I have been warned it will kill me. Still waiting for that, I think.
 
Last edited:

dc655321

Major Contributor
Joined
Mar 4, 2018
Messages
1,597
Likes
2,235
Unless your "dedicated mains for audio" come directly from the power plant, bypassing anyone else hanging a load off it, there are bigger fish to fry.
I would not worry one iota about any of those things.

Also this: audio devices do not typically (ever?) use AC signals directly without rectification and conditioning. There is little one could reasonably do external to their audio devices and even less internally.
 

Shadrach

Addicted to Fun and Learning
Joined
Feb 24, 2019
Messages
676
Likes
980
If your in the UK you have a ring main. I don't know what the standard is in the USA.
Here in Europe we have a radial system and I have a separate spur from the fuse box to a two pin outlet.
Ring mains have their own particular problems. Noise from household appliances injected into the ring for example.
Can you hear it? I could when I was in the UK. I did what you are suggesting and lost the clicks and pops.
Here in Spain it's not so much of a problem.
 

DonH56

Master Contributor
Technical Expert
Forum Donor
Joined
Mar 15, 2016
Messages
7,891
Likes
16,699
Location
Monument, CO
This is all USA-centric.

There are plenty of things in a house that can generate hash on the AC power lines. I have dedicated lines to my media room but they all tie at the service; bringing in a separate mains supply just moves the tie point a little further and would cost me a fortune to install and then for the separate monthly bill. No thanks.

Grounding requirements are usually per code. Adding another ground rod may or may not be to your local code, and may create an unwanted ground loop. I would not bother.

Things I do usually advise:
  1. Run 20 A circuits, preferably 2-3 circuits, for a dedicated media room. Those are for front, rear, and side wall outlets. Include a separate dedicated line (15 A fine) in the ceiling for a projector just in case. Lights are normally on a separate circuit but make sure. A separate sub-service for the media room is nice if you can -- makes it easier to kill power when you are mucking around in there.
  2. One thing I did was wire the upper outlet of a duplex to a light switch. No holes in the ceiling for lights (my room is isolated so tried to minimize holes) and you can flip a switch at the door to turn on floor lamps or sconces.
  3. Add whole-house lightning and surge protection (those are two different units) at the incoming service.
  4. Make sure there is lightning protection on the cable coming into the house (ours did not; they added it -- with a separate local ground rod 10' long -- after a near strike took out the cable box -- the whole-house protection saved everything else).
  5. Our power is spotty and we have short (few seconds) to long (~week) outages often enough that I bought UPS units for all my critical electronic stuff (TVs, stereo systems, computers, aquarium pumps, etc.) They also provide some filtering but their main purpose is to ride out a short outage and allow me to shut things down gracefully if it is longer. I used APC for ages but got aggravated and now have several CyberPower units that seem to do OK. TrippLite is another big name.
  6. Not electrical, but if you are building a dedicated room, look into Kinetics Noise COntrol IsoMax clips or similar and isolate the room. I did that and added a minisplit HVAC unit so there are no HVAC ducts (which also work great at carrying sound) to the rest of the house.
Sure there are tons of other things but my 0.000001 cent (microcent) - Don
 

RayDunzl

Grand Contributor
Central Scrutinizer
Joined
Mar 9, 2016
Messages
13,250
Likes
17,186
Location
Riverview FL

DonH56

Master Contributor
Technical Expert
Forum Donor
Joined
Mar 15, 2016
Messages
7,891
Likes
16,699
Location
Monument, CO
I think ring circuits are actually against US codes but waaay too long since I passed that test and worked as a journeyman electrician... All changed now anyway.
 

RayDunzl

Grand Contributor
Central Scrutinizer
Joined
Mar 9, 2016
Messages
13,250
Likes
17,186
Location
Riverview FL
Back to the real world:

My outlet for the gear is on a chain with several other outlets spread around the room and near the kitchen...

The rack runs off a single 15A outlet on that chain, which is severely overloaded in terms of maximum draw, works fine for daily use.

PC stuff is on the same circuit...

The kitchen 8-tube fluorescent lights are on the same circuit (I hate houses)...

If I run the vacuum cleaner and the Krells and the Plasma TV and the PC and kitchen lights the breaker pops right away.

Two years ago I bought the hardware to add a dedicated outlet (80 feet to the breaker box). Haven't installed it yet, lazy.

Never noticed any noise from the speakers due to "power".

Did notice transformer groaning before adding the Equitech - assume either DC or unbalanced AC waveform.

Caught the Utility delivering low voltage and got them to replace the local transformer by the street with a beefier unit.
 
Last edited:
OP
B

babysnake

Member
Joined
Oct 30, 2018
Messages
40
Likes
14
Caught the Utility delivering low voltage and got them to replace the local transformer by the street with a beefier unit.

Dude that is real power and influence !!!!

I think the standard UK wiring scheme of having a 'ring main' is, for our particular purposes, suboptimal as I am sharing my kit with mains that has cookers, PCs, phone chargers and all sorts of other junk plugged in. My wife's hair straighteners upstairs make my amps hum !!

I'm thinking a 'dedicated' spur at least gets me away from that

Just reading @amirm's review of the Entreq now ...
 

Willem

Major Contributor
Joined
Jan 8, 2019
Messages
3,722
Likes
5,353
My late father, an electical engineer of some repute, always said that mains in the US was far worse than in the EU given the different design of the network and the outdoor cabling. Sadly, it is too late to ask him for an explanation, however. To be honest, here in the Netherlands I have never experienced anything remotely problematic.
 

tdflance

Member
Joined
Apr 17, 2019
Messages
8
Likes
7
Back to the real world:

Caught the Utility delivering low voltage and got them to replace the local transformer by the street with a beefier unit.

Curious as to what low voltage you were getting?

I'm in the US and our house is mid century. When we moved in and I setup my sound system, I kept hearing a ground loop issue. I ran 3 dedicated 20 amp circuits for my system. Ground loop gone. However, my voltage still only reads 117volts. Should I be concerned? Thanks
 

DonH56

Master Contributor
Technical Expert
Forum Donor
Joined
Mar 15, 2016
Messages
7,891
Likes
16,699
Location
Monument, CO
ANSI C84. Service is what the utilities must provide and Utilization is what should be at your house. The NEMA standard is what components are supposed to meet (+/-10%).

https://www.pge.com/includes/docs/p...ergystatus/powerquality/voltage_tolerance.pdf

1555530508567.png
 

tdflance

Member
Joined
Apr 17, 2019
Messages
8
Likes
7
Cool, appears I'm in the "zone" then. Thanks for providing, good info. Amazing that for 120 volt standard can deviate/drop as low as 104....
 

Shadrach

Addicted to Fun and Learning
Joined
Feb 24, 2019
Messages
676
Likes
980
Dude that is real power and influence !!!!

I think the standard UK wiring scheme of having a 'ring main' is, for our particular purposes, suboptimal as I am sharing my kit with mains that has cookers, PCs, phone chargers and all sorts of other junk plugged in. My wife's hair straighteners upstairs make my amps hum !!

I'm thinking a 'dedicated' spur at least gets me away from that

Just reading @amirm's review of the Entreq now ...
The ring main was and is a terrible idea. Apart from being a shock hazard any noise generated on one part of the ring ends up everywhere else on the ring.
In Europe I beleive everywhere has radial circuits; hence not needing fuses in plugs (that alone can save you a few hundred pounds on audiophile fuses:p)
In a radial circuit each outlet returns to an RCD in the fuse box which is a lot more sensible.
 

RayDunzl

Grand Contributor
Central Scrutinizer
Joined
Mar 9, 2016
Messages
13,250
Likes
17,186
Location
Riverview FL
Dude that is real power and influence !!!

Measurements matter.

They size the local gear based on expected demand.

After 6 years, demand of the six or eight houses on that transformer apparently increased.

I sent the Utility Engineer that responded to my complaint a log from my cheezy UPS that registered 122V overnight and sags to 108V during the heat of the afternoon in August.

1555533969949.png


They hung a recording meter on the entrance for a month, read the data, agreed the service didn't meet spec, and replaced the transformer.
 

RayDunzl

Grand Contributor
Central Scrutinizer
Joined
Mar 9, 2016
Messages
13,250
Likes
17,186
Location
Riverview FL

tdflance

Member
Joined
Apr 17, 2019
Messages
8
Likes
7
I see that. Thank you. Makes me wonder how many hoods have this happening without any action to change until a consumer takes on their own research and provides data like you. Nice.
 

tdflance

Member
Joined
Apr 17, 2019
Messages
8
Likes
7
Apologize in advance of the article below but this web page is no longer available (it redirects) so i copied and pasted here. This is basically the prescription I followed when I installed dedicated circuits.
Improving your Listening Room Wiring - By Vince Galbo
VinnyCES08_1.jpg

NOTE: Please note that the details of these recommendations are written from the perspective of the American market - 120V system. Please make the appropriate adjustments for a 240V system.

WARNING: Please read this recommendation fully and then get an electrician to agree to do the work. If you decide to do this yourself then decide if you have actually done this kind of house-voltage electrical work before and are competent to do so and accept the risks of doing so. MSB or Vincent Galbo makes no guarantees or accepts any responsibility for any injury or the results or any damages caused by considering or performing the procedures outlined below. MSB or Vince Galbo make no guarantees the information is correct or complete. Rely only on the services of qualified personnel to interpret the information and perform it safely. The reader of this document is responsible to decide who is qualified to perform the work. The reader of this document is responsible to determine if any of these recommendations are in violation of any local codes.​
How to wire your house for improved audio and video performance - What is the Goal?
In many cases depending on the oxidation of connections, age of the breakers, length and gauge of the wall wiring, the above wall power changes in your home system are often a bigger improvement than any component that you can buy, especially with solid state amps. But even people with tubes report improvements if not big improvements.

People often tell me "I have 20 amp dedicated lines". By US electrical code definitions, a 20 amp dedicated line will have 12 gauge wire in the wall. So while you may have a "dedicated line", 12 gauge wire is absolutely insufficient for high end audio systems. We are recommending ten gauge or thicker wire here. It is the subject and goal of this paper. The gauge of the wire is FAR MORE IMPORTANT than the fact that the line is "dedicated". The subject of this paper works on the theory that the varying musical demands of your amplifier are actually modulating the incoming power line, divorced from the utility (power company) by some resistance (12 or 14 gauge wall wiring at some length from the breaker panel has too much resistance for audio purposes). The noise coming from your utility is probably much lower than you suspect and the gauge of the wire is far more important. The amp demands current up and down with the music at audio frequencies that are of course above and below the 60 cycles from the power company. These demands are impressed on the line wavering the incoming voltage and so the amp is re-ingesting its own noise and also making the line dirty for itself AND the audio front end. This is possible because the wall wiring back to the breaker panel has some degree of resistance depending on the length of the run and the wire gauge (12 gauge or sometimes even 14 gauge). Power conditioners and certain power cord designs help because they make an effort to "shunt" this noise (short it out and kill it) and consume the unwanted frequencies. A better answer is to reduce the resistance back to the breaker panel making it difficult for the amp to modulate the power at all and also at the same time getting maximum power for the amplifier power supply. And so there are two benefits to reducing the resistance back to the breaker panel.
The Main Goal - Lower Resistance
The single biggest goal in improving audio is to install heavier gauge wire using the following guide.
  • 1 to 40 feet: 10 gauge wire
  • 40 to 60 feet: 8 gauge wire
  • Over 60 feet: 6 gauge wire
Everything else in this paper is there to be sure you get the maximum benefit from the lower resistance of heavier wire! Skipping any steps is false economy.
Silver Paste Selection
silverPaste_SL1500_.jpg

Silver paste is important to reduce contact resistance. These pastes are called 'grease' but be wary of any that are actually that fluid. I have reports of migration of at least one audiophile silver grease that, because of voltage potential across the Line and Neutral attempts to migrate and close the gap between the hot and the ground. In one local attempt it burned up an outlet. That is why I use the McMaster Carr product. It is almost crumbly and never migrates upon inspection years later, nor does it seem to oxidize over time. There are reports of audiophile silver pastes that do oxidize and so the oxidized silver becomes worse than not applying silver at all. DO NOT try to use this stuff on interconnects, etc. While it could be a good thing, it is impossible to control it and it smears around in use because it never really dries. The result is a partial or complete short across signal hot and ground. I added this comment based on one audiophile who tried it on his interconnects, got no sound in one channel, weak distorted sound in the other, and spent hours washing his RCA plugs and cleaning his input/output jacks on his components. I don't think it can be completely cleaned out and he should have replaced the jacks and plugs. In other words just don't do it. Here is our first and second recommendation.
  1. McMaster
  2. Amazon
The McMaster is a pure silver paste in a minimal amount of carrier. This is the best of the silver products to use at about $85. It will last for years since you only need a very small amount. The second choice is a possible, less expensive alternatives.

Silver Paste Application
You will use the silver paste at every AC power connection that is made starting by removing the breakers and applying it to the inside of the clip on the back of the breaker. No need to apply it to the buss bar connection especially since these are always live!!! The clip will transfer the paste to the buss bar. You will also use the silver paste on the wires where they enter into the screw terminals both at the breakers and the duplex outlets. A thin film is all that is needed on all these connections and the silver actually performs better as a thin film. This stuff tends to get on the fingers and then everywhere else so be sure to clean up with Goo Gone or some such solvent since it is like liquid wire. It can be a finger-shock hazard if you are sloppy with it, so be sure to clean up any excess or smeared film with a solvent like Goo Gone even if you can't see it. Your electrician will have a non corrosion paste that he always uses to preserves the copper connection but does not reduce the resistance of the connection anywhere near as well as the silver paste. The electrician's paste is not suitable for our purposes. The silver or a silver-loaded copper compounds are the only choice.
Circuit Breaker Replacement
CircuitBreaker.jpeg

I recommend new breakers if they are older then one year or so. (they are cheap). If you get the original equipment circuit breakers (like Square D, Siemens, etc.), from an electrical supply house (not Home Depot or Lowe's), you will likely get silver-tungsten contacts inside the breaker. Cheap replacement breakers are likely to have copper contacts which have higher resistance and will oxidize over time raising the resistance further. Research with your local electrical supply and ask them to look up the breaker contact material to confirm it is silver or silver tungsten.
New Circuits
I recommend at least two 20 amp 120 volt circuits sized based on the distance of the run.
  • 1 to 40 feet: 10 gauge wire
  • 40 to 60 feet: 8 gauge wire
  • Over 60 feet: 6 gauge wire
The 8 gauge (or 6 gauge) requires a jump-down back to 10 gauge using a junction box, somewhere just before the outlet because the largest wire that will fit in an outlet is 10 gauge. Install one dedicated line for all front end equipment, and one for each amplifier. If you must feed old branch circuits off one of these outlets, it is not absolutely necessary that your audio lines are dedicated lines as long as the wire path at the outlet you are using goes directly back to the breaker panel using 10 gauge or heavier wire. The circuit can branch to other outlets from your audio outlet if necessary. (some people won't agree with this).
Select Same Phase
panel.png

For 120 volt circuits: MAKE SURE ALL EXISTING AND NEW CIRCUITS THAT YOU USE ARE ON THE SAME ELECTRICAL PHASE. I have had several direct experiences with an audio system connected on both electrical phases and the dual 120 volt feed from the electrical grid seems to make a good antenna to pick up RF. Connecting your system to only one electrical phase seems to prevent any RF issues that can damage equipment in areas with high RF. (No� you have no way to know if you are in a microwave path, or TV/radio transmission path, just do it!) Usually, every other breaker in the stack is the same phase. In other words, starting at the top (first) breaker in the left column you will have 'A' phase. The next breaker down (second) will be 'B' phase, and then the next (third) will be 'A' phase again, etc. So the two dedicated lines should be spaced one breaker apart to be on the same phase. Some newer panels may have one phase all on the left, and the other phase all on the right. If you don't know have an electrician help or do the work. Decide if you are competent with an AC voltmeter and you will not be dangerous to yourself. If you have experience with an AC voltmeter measuring wall power and you feel you are competent then you can test between any two outlets to prove they are on the same phase by testing for AC voltage across the two shorter slots in the respective wall outlets. (the longer slot is always the neutral). Measuring between the two outlets probing their respective short slots you should have a reading near zero volts and maybe floating around several millivolts (mv). If your reading is 220-240 volts then the two outlets are on opposite phases and should be corrected.
Tighten Up the Connections
It is a good idea to ask your electrician to go around the breaker panel when he is done and tighten all of the set-screws that clamp the wires. This is especially important on the heaviest cables that feed the panel. These screws will be LIVE! so ask the electrician if he has the proper voltage-rated insulated tools to do this and if he is comfortable doing. Electricians will often do this any time they service a panel. DO NOT pick up the tools you own with the plastic or rubber grips and think you can do this yourself. Your tools are not rated for this procedure and it is fatally dangerous if you make a mistake, so DO NOT be tempted. Let an experienced, qualified, licensed, insured, person do this.
Replace Outlets
HubbleHospitalOutlets.jpeg

Try to find Hubbell hospital grade outlets with isolated grounds or something like the PS Audio Power Port, or Furutech. Generic commercial grade outlets are not a good substitute. Low and medium priced audiophile outlets are a good investment since they are heavier copper, better plated and really grip the blades of your power cord plug. I have no opinion about the very high priced cryogenic, etc., outlets. The isolated grounds can be run back to the panel individually.
About Power Conditioners
I don't recommend line conditioners on amplifiers when the system is done as described above. It is generally better to go straight into the wall. But if you do use a line conditioner be sure it has NO CURENT or WATTAGE LIMITS and it is a straight-through design with any filtering elements ACROSS the line. If it does have a wattage or current rating then it would indicate some sort of treatment in SERIES with the line which is almost never, ever good for amplifiers and may even choke off lower power gear like front ends depending on the design of the conditioner. I do recommend conditioning for all front end equipment. For front ends which tend to draw little power compared to the amp, you might pursue a clever conditioner that does have elements in series but do be concerned about power limiting. (use your ears). If you only run one wall power line, plug the amp direct into the wall and then the front end into your line conditioner. It is better to install two lines (which must be on the same phase) because the amplifier will modulate the wall power fluctuating by the demands of the music and actually make noise on an otherwise quiet wall power line. Plug the amp direct into one and a line conditioner into the other which you will then plug your front end into. The Shunyata line conditioners and the Richard Gray are two good ones that I have used for amplifiers because they are straight through. I prefer the Richard Gray because they actually lower the impedance by storing some power on every AC cycle and they correct an error on the line known as 'power factor error'. So the RG 400 is the best for amplifiers. Unfortunately 2 or 3 RG 400s are needed 'star clustered' together to get the collective impedance low enough to be effective for an amplifier. One RG 400 alone doesn't do much for big amplifiers. The amp should be plugged in the wall with the RG 400s. This requires a quad box or a high quality audiophile power strip. (Since this paper was written in 2001 many line conditioners have come on the market. I believe the general theory above still holds true. Look for straight-through unlimited current-wattage for amps, then high current excellent filtering for front ends). Shunyata is another company that is dedicated to straight through design. They seem to concentrate more on shunting the noise that has already been generated and may do this better than the RG 400. Lately I am using both types together at the audio shows where I cannot do anything about the wall wiring. The RG400s provide low impedance behaving more like the system is connected closer to the breaker panel, and conditioners like the Shunyata quiet the high frequency noise from both the amplifier-modulation and the wall power noise. Even more recently I have had success with BIG isolation transformers. They should have a VA rating at least double the 'va' (volts-amps) rating of your amplifier transformers. Triple the rating is better, so if your amp has a 1000 va (which is 1 kVA) transformer, the isolation transformer should be 2000 (2 kVA) minimum and may be marginal, 3000 to 5000 va (5 kVA) is better. I only mention the subject of line conditioners and isolation transformers to be complete. I prefer the amps straight in the wall and try line conditioners on the front end before you buy one.
The 240V Option
Nema6-20Receptical.jpeg

Some high end amps can be switched over and run on 220 volts and I recommend it may sound better. The transformer primaries and the core seem to run slight more efficiently yielding lower impedance so the supply might appear slightly 'stiffer' to the amp's audio circuits (always a good thing). Because the amp is now running at twice the voltage but half the amps (current) the wall wiring looks twice as thick to the amp as it does at 120 volt (ohms law). Now the amp makes even less audio noise on the line and it then rejects its own line noise better. The 220 volt outlet can be a standard 15 amp with 10 Ga.. Wire up to 80 feet then 8 gauge beyond that.

For the 220 volt lines, the electrician may, or may not know about a NEMA receptacle and plug number that is the same size and form as our common Edison duplex 120 volt receptacle but the wide blade of the plug is on the opposite side as the 120 volt duplex. Hubble or commercial Leviton works fine for 220 volt, and the 6-20 series looks less industrial in your home.

It is Nema plug number 6-20P. 'Stay on line' is a good source but your electrician may like a local supplier.

BE SURE TO CHANGE OVER THE AMP INTERNALLY IF YOU DECIDE TO RUN 220 VOLT !
Last Trick - Twist the conductors
Lastly, you might ask him to twist the conductors one twist every 6-8 inches or so. Each line should be alternately twisted relative to the one next to it. This prevents any coherent coupling between them. Keep them away from each other by minimum 4 inches. It is perfectly OK to cross them at a right angle.
Final Word
If your electrician has any concerns about all this, be aware he is always concerned about CONTINUOUS current draw and rates everything and splits up the loads like the air conditioning and the electric dryer for the available amperage. Please explain to him that we are designing for incredibly short peak current pulses and we need the resistance back to the utility as low as possible for best amplifier performance. The continuous draw is negligible from an electrical standpoint. 10 gauge wire is the largest size that will fit into a wall outlet and as far as I know does not violate any codes but you and your electrician are responsible to be sure this is true in your state, county, and city.

Be sure that your speaker cable is at least 10 gauge. You should consider 8 or 9 gauge for speakers that are below 87db sensitivity, and/ or 4 ohms. Some manufacturers say, 'our 14 gauge behaves like 10 gauge, etc.', this could be true but I go for the real measured gauge.

Now, without exception over the last 12 years, comments from those that have done the above heavy gauge wire wall power mods say there is audible improvement in dynamics while making the sound even more detailed, yet much more relaxed with dark backgrounds leaving only the notes and music. I was very surprised the first time I did this house power mod. I did not expect the mid-range and the highs to clean up and get more coherent as much as they did. Of course bass and dynamics are better as you would expect with better current delivery.
 

blackmetalboon

Active Member
Joined
Dec 18, 2016
Messages
139
Likes
173
Location
UK
1. A dedicated radial circuit is probably what you require. Cable and MCB/fuse size will vary on various factors. Don’t bother with a dedicated Consumer Unit, it is pointless.

2. No, this can open a whole can of worms. Depending on which earthing system your property uses, certain fault conditions can cause dangerous situations.

3. Do you have more money than sense?;)

4. There are maximum and minimum voltages allowed in the UK, if yours fall outside these then the Electrical Network provider has to rectify this. Most modern kit will work fine within the permitted voltage range.

In general, ignore pretty much all electrical advice on forums that is accompanied by subjective impressions of how their sound quality improved.
 

Timbo2

Senior Member
Joined
Feb 27, 2018
Messages
497
Likes
396
Location
USA
Measurements matter.

They size the local gear based on expected demand.

After 6 years, demand of the six or eight houses on that transformer apparently increased.

I sent the Utility Engineer that responded to my complaint a log from my cheezy UPS that registered 122V overnight and sags to 108V during the heat of the afternoon in August.

They hung a recording meter on the entrance for a month, read the data, agreed the service didn't meet spec, and replaced the transformer.

I did the same thing - here in the corrupt people's republic of NJ it took 18 months of me arguing with JCP&L to get the transformer replaced / re provisioned.

Another time my voltage on one leg was 90V and the other was around 106V. Tried to report it and naturally nothing on the automated phone tree had anything that would let you actually report low voltage. Somehow trying to go through the phone tree I must have accidentally reported a fire or short. Went to bed got woken up in about 30 minutes by a lineman at the door.

Apologized profusely and explained the issue. He said no worries and measured the voltage and agreed with the issue. I thanked him and went to bed. Woke up the next morning with the guys still working on the line and another two additional trucks.
 