In the unlikely event your single speaker ever actually draws this amp's maximum power, it could only be for the briefest of transients. Even with two of them, that's unlikely to trip a breaker. Your typical breaker operates thermally, and briefly (as in for milliseconds) exceeding the amperage will not immediately trip it (and is perfectly safe for the wiring).
If you want to get more technical, you can research circuit breaker trip curves:
View attachment 501917
The breakers in your load center are likely of the C curve variety. The X-axis is multiples of the rated capacity (typically 15A or 20A). As you can see (if you squint, sorry for the low res image), at 5 times the rated amperage (so 75A or 100A) it would take at least a full second for the breaker to trip. This is actually a good thing, as otherwise the inrush current from the compressor on your fridge or the motor on your vacuum would be constantly tripping the breakers.